090227-1432 EST
I ran two experiments with my test Leviton GFCI.
The GFCI was fed with two wires only, but there was a ground wire in the 20" long cord to the GFCI. Two different transmitters were used. A Motorola Talkabout T5720 on channel 1 (high power 1 W). And a Kenwood TR7625 2 meter 25 W transmitter at 145 mHz.
The Motorola with its antenna in immediate contact with the GFCI input cord could not trip the GFCI.
The Kenwood in 25 W mode with a 1/4 wave antenna (about 20" long) parallel and close to the GFCI input cord could not trip the GFCI until the antenna to cord spacing was within about 1/2 to 1".
I would classify this GFCI as moderately immune to RFI.
.