Most likely a boilerplate specification value.
I agree but I have seen numbers that high and higher on services connected to a POCO UG grid but they are usualluy sizable services (amps) with short supply conductors.
 
65kA fault current on a 208Y120 system? How big is your transformer, > 1MVA?
I agree but I have seen numbers that high and higher on services connected to a POCO UG grid but they are usualluy sizable services (amps) with short supply conductors.
I had a recent job served by 3x 166 KVA submersible units, 1.7% imp. Do the math....
 