Most GFI requirements are for dwellings, which typically aren't 3-phase. And what is required to be GFI protected in a commercial setting usually uses SP breakers or GFI receps.
OK, so it would theoretically be possible. This is in an industrial setting where a GFCI is not required, but Safety has asked for one. The receptacles to be protected are all on the same MWBC, so a 3 pole GFCI would have saved a lot of time.
One could legally use a 3-pole GFI breaker, but I would be, IMPO, a poor design. One circuit has a fault, and it keeps two others from working.... not good when serving food is what pays your bills.
Whats the difference between this and a fault on one pole of an mwbc. Still going to have one single phase component trip three circuits.
They do make 3 phase circuit breakers!!! There are a bunch of them on this campus and they are safe but a PAIN!~ We had a controls tech turn on a circuit that had a shorted radiant heat panel on it. Lost the entire building due to the main being GFCI. In the gym, one outside step light shorted and tripped the breaker in feeding the 42 circuit, 277 lighting panel. The entire floor went dark.
Sounds like you are talking about GFP, not a GFCI.
SQ "D" calls it GFCI in the catalog???
To interrupt a quote, you need to type [/quote] where you want the quote to halt, andOK, apparently I did that wrong. My response to the first sentence ended up in the middle of the quote.
where you want it to start up again.
That's what I thought too, GFPE. Ground fault protection equipment, 30 ma trip.
When ground fault tripping is done above the mA range, the device is often called a GFI. And of course GFI becomes mis-spoken as GFCI often.not the 30ma trip for equipment protection, it was mains that were tripping. GFP in the hundreds of amps range. Keeps you from burning up an entire run of shorted bus duct when supplied with a 5000amp breaker (oh wait :/)