bill@usps06492
Member
- Location
- Connecticut
I've installed a 2-pole gfci CB 30a 240v in a panel. With no load, and no wires attached to this circuit breaker it will trip as if it has an overload. The original gfi breaker was doing the same thing and so I replaced it thinking it was faulty. Now I'm scratching my head. The service I'm working on is a 3phase 120/240v with a 208 high leg. I checked for any volts between neutral and ground, my meter showed 0vac. I've moved it off the high legs, it still trips. There isn't a ground wire from builing steel or the water main to the panel, it's a 4 wire main lug, its an older service, but there is a ground bar in the panel. There is no grounding wire run wire the 4 wire feeders. I assume it is all bonded at the service disconnect. On a 240v gfci what do you do with the white pig tail? The manufacturer(GE THQB) states not to attach it to the neutral if there is no neutral used, but its vauge on what to do with the pig tail. There isn't a neutral load, it is for a 1ph 240v stationary wet saw used to cut concrete blocks, but if I don't attach the pig tail to the ground or neutral bar, when I hit the test button on the gfci, it will not trip. But even with the pig tail not tied to the neutral or ground, the gfci will still trip as if it is sensing an overload. Any ideas ??? Bill