slick 50
Senior Member
- Location
- 6 super bowl ring city
You must always connect the pigtail neutral regardless of 240v or 120v applications because this is the neutral connection that powers up the electronics on the internal board which is what makes it an electronic sensing breaker. A 2 pole GFI breaker is only for 240v loads. If you were feeding a 120v load, you use a single pole GFI. On the 2 pole GFI, there is a termination point for two load hot conductors and one load neutral conductor. The load neutral does not have to be used if there is not one in your branch circuit. If you leave the pigtail disconnected, the breaker will act the same as a standard thermal magnetic 2 pole breaker which will trip on short circuit and overload situations. To determine if the breaker is good, connect pigtail to neutral bar and install with no load wires connected, now turn breaker to on position, if it holds then push the (PTT) push to test button and if it trips, the breaker is good. Now connect your load wire to breaker and turn breaker to on position with load turned off. If it is still holding, good. Now turn load on, if it trips instantly, you have 4 plus milliamp of GF leakage either in the load itself or in the branch conductor.