deviltrini
Member
- Location
- riverview, florida USA
So today I came across a GFCI combo 15amp breaker that would not trip when I pressed the test button. Typically that means bad breaker however today that was not the case. I changed out the breaker with 3, 2 of which I knew for a fact worked just fine. The circuit can be tripped from inside the home with my plug tester. The test button also worked when either the hot or neutral was removed from the breaker but not when both were tied in. Has anyone ever came across this if this what was the problem? I thought it may be a circuit that was not completed? Not to sure however I replaced the breaker with a 15amp Arc-fault and the test button worked just fine. I am sure someone must have came across this before. Any feedback would be great. Thank you