About how much can I expect?, Also what is the trip current for a class A GFCI, I ask because I was troubleshooting something at my parents house and was measuring about 20 mA.
 
About how much can I expect?, Also what is the trip current for a class A GFCI, I ask because I was troubleshooting something at my parents house and was measuring about 20 mA.

I don't know how much they draw but a GFCI should trip at around 4 to 6 ma.
 
No problem, I am just passing it along from the FPN after the definition of Ground Fault Circuit Interrupter in Article 100.

Didn't even look there.

From Gar:

"the tripped state the 120 V input current is 10.4 MA and an orange LED is on. After RESET the input current drops to 6.2 MA and the LED is off.
"

so could a gfci installed on another gfci trip the first?
 