GFCI for electric pool water heater

Status
Not open for further replies.
IMHO, just because there are no Code sections that say you have to GFCI protect the circuit doesn't mean you shouldn't. Here the Code doesn't require you to GFCI protect it.
680.10 Electric Pool Water Heaters. All electric pool water heaters shall have the heating elements subdivided into loads not exceeding 48 amperes and protected at not over 60 amperes. The ampacity of the branch-circuit conductors and the rating or setting of over-current protective devices shall not be less than 125 percent of the total nameplate-rated load.
Yet, when you get down to this Code section for gas fired heaters it does :
680.28 Gas-Fired Water Heater. Circuits serving gas-fired swimming pool and spa water heaters operating at voltages above the low-voltage contact limit shall be provided with ground-fault circuit-interrupter protection for personnel.
It doesn't make sense to me. From a standpoint of safety - I would GFCI protect it
 
If not a permanently installed pool I think 680.32 requires GFCI protection.

Permanently installed pool - GFCI not necessarily required, but probably still a good idea. It must still be connected to the equipotential bonding system. Doing that ensures it remains at same potential as the rest of pool equipment when a fault occurs.
 
There simply is no req. for gfci on pool electric heater and the gas fired is only required in some cases. This is new to the 2017

680.28 Gas-Fired Water Heater. Circuits serving gas-fired
swimming pool and spa water heaters operating at voltages
above the low-voltage contact limit shall be provided with
ground-fault circuit-interrupter protection for personnel.
 
There simply is no req. for gfci on pool electric heater and the gas fired is only required in some cases. This is new to the 2017
OK, but stop and think about the logic of this - if you're mandated to GFCI protect a gas fired heater why wouldn't you also be mandated to GFCI protect an electric heater ? Is it something the CMP's just missed ? With respect to 680.28 in what cases would you not be required to GFCI protect a gas fired heater ?
 
OK, but stop and think about the logic of this - if you're mandated to GFCI protect a gas fired heater why wouldn't you also be mandated to GFCI protect an electric heater ? Is it something the CMP's just missed ? With respect to 680.28 in what cases would you not be required to GFCI protect a gas fired heater ?
If they don't operate above the low voltage contact limit.
 
OK, but stop and think about the logic of this - if you're mandated to GFCI protect a gas fired heater why wouldn't you also be mandated to GFCI protect an electric heater ? Is it something the CMP's just missed ? With respect to 680.28 in what cases would you not be required to GFCI protect a gas fired heater ?

My first guess is that the "normal" leakage current, including capacitive current, of a typical electric submerged element heater is high enough to cause nuisance tripping of a GFCI?
 
My first guess is that the "normal" leakage current, including capacitive current, of a typical electric submerged element heater is high enough to cause nuisance tripping of a GFCI?
We use them in hot tubs all the time and GFCI protect those. Most common cause of hot tub GFCI tripping from my experience is from faulted heating elements.

Still as I mentioned earlier in a permanent pool the thing still needs to be bonded to equipotential bonding system. Whether or not GFCI is used, that bonding is what provides the most direct protection to pool users. If the heater housing becomes energized, the entire EPB system raises to the same level.
 
680.28 Gas-Fired Water Heater. Circuits serving gas-fired swimming pool and spa water heaters operating at voltages above the low-voltage contact limit shall be provided with ground-fault circuit-interrupter protection for personnel.

As with most new NFPA code, application of 680.28 is ambiguous in the field.

The ambiguity bomb of 2017 NEC 680.28 is, "operating at voltages above the low-voltage contact limit"

1) Hot water circulated by electric pumps operating > 100vac need GFCI protection. - OK.

2) Gas heaters operate fuels/ignition/temperatures using low-voltage controls, so no GFCI needed for 24vac. - OK.

3) Low-voltage contacts operate by transformer. - Must xformer primary >100vac be on GFCI? - Application is ambiguous in the field.
a) The ambiguous term "personnel" does not clarify, since it could be maintenance persons, pool users, or both.
 
Most transformers for pool equipment are specially designed so that there can be no contact between the line side and the load side.
 
Most transformers for pool equipment are specially designed so that there can be no contact between the line side and the load side.

Exactly, so why interpret this code to require GFCI's on line-side of transformers?

Unless all equipment enclosures, j-boxes containing line voltages, or xfmr failures in closed position, must be anticipated?
 
Last edited: