On a floating boat dock at a residence is GFCI protection required for the lighting?
Thanks
Don
Thanks
Don
On a floating boat dock at a residence is GFCI protection required for the lighting?
Thanks
Don
On a floating boat dock at a residence is GFCI protection required for the lighting?
Thanks
Don
I strongly suggest that the circuit be GFCI protected before it leaves land. Most kids getting killed on docks are not killed by the load but by the circuit under the dock or otherwise.
Am I the only one that thinks this is required, and not just a suggestion? Like you said, and alot people have died because of this issue.
On a floating boat dock at a residence is GFCI protection required for the lighting?
Thanks
Don
Am I the only one that thinks this is required, and not just a suggestion? Like you said, and alot people have died because of this issue.
Provide us with a link that requires it. It is not a marina, nor a floating building so where would it fall. I don't see this as fitting under any special requirement but perhaps it should.
Provide us with a link that requires it. It is not a marina, nor a floating building so where would it fall. I don't see this as fitting under any special requirement but perhaps it should.
682.1 Scope. This article applies to the installation of electrical wiring for, and equipment in and adjacent to, natural or artificially made bodies of water not covered by other articles in this Code, such as but not limited to aeration ponds, fish farm ponds, storm retention basins, treatment ponds, irrigation (channels) facilities.fmtjfw said:555.1 Scope. This article covers the installation of wiring and equipment in the areas comprising fixed or floating piers, wharves, docks, and other areas in marinas, boatyards, boat basins, boathouses, yacht clubs, boat condominiums, docking facilities associated with residential condominiums, any multiple docking facility, or similar occupancies, and facilities that are used, or intended for use, for the purpose of repair, berthing, launching, storage, or fueling of small craft and the moorage of floating buildings.
Private, noncommercial docking facilities constructed or occupied for the use of the owner or residents of the associated single-family dwelling are not covered by this article
682.1 Scope. This article applies to the installation of electrical wiring for, and equipment in and adjacent to, natural or artificially made bodies of water not covered by other articles in this Code, such as but not limited to aeration ponds, fish farm ponds, storm retention basins, treatment ponds, irrigation (channels) facilities.
Dennis, since it is not covered by 555.1, then 682.1 would apply.
All circuits not more than 60 amps 125 to 250 volts single phase shall have GFCI protection.
Actually, it is the docks that are not covered, not the bodies or water. A grammar and logic question which can probably support another 20 posts.
IMHO 682.1 does not apply.