tallgirl said:Well, I'll see your cartidge and raise you 210.52 (B) (2) exception 2.
How does that apply to an Individual Branch Circuit installed under 210.52 (B) (1) exception 2, which has become the topic of this thread?
Last edited:
tallgirl said:Well, I'll see your cartidge and raise you 210.52 (B) (2) exception 2.
Mike03a3 said:How does that apply to an Individual Branch Circuit installed under 210.52 (B) (1) exception 2, which has become the topic of this thread?
I'm not making the connection on two counts:tallgirl said:Well, I'll see your cartidge and raise you 210.52 (B) (2) exception 2.
The individual branch circuit for the fridge in the exception to (B)(1) is not a SABC.tallgirl said:Where's the hole in my argument?
Nobody suggested it was.iwire said:You all are taking a simple thing and making it way to difficult.
First off this is not a safety issue.
Ah, but it's a CODE issue. That's what we're discussing hereIf an item was intended to run on an individual branch circuit and it ends up sharing a circuit the worst case is a tripped breaker.
A tripped breaker can happen on any multi outlet circuit.
Next is you have to stop thinking that individual branch circuit has anything to do with the number of receptacles on a circuit.
Also keep in mind that the definition of individual branch circuit was not written only for dwelling units, there are many other flavors of receptacles other than 15 and 20 amp 125 volt receptacles.
georgestolz said:I'm not making the connection on two counts:
1. I don't get the code reference, and
2. Are we playing cards or shooting long dead horses?
![]()
Mike03a3 said:I'm also confident that in the specific case of a dwelling, and the use of the exception allowing an individual branch circuit in lieu of supplying a refrigerator with one of the small appliance circuits, an inspector is on solid ground rejecting a duplex receptacle. The inclusion of a second, unused, receptacle, not required for the single permitted utilization equipment (refrigerator), makes it a General-Purpose branch circuit by definition and thus not allowed under the exception.
tallgirl said:Which says, to me, that an IBC for a fridge can have an extra outlet for a clock and still be an IBC.
iwire said:(Bob slamming head against wall) An IBC does not need an exception for more outlets, it only needs an exception for more equipment!!
tallgirl said:Code reference was off by one exception. It should have been exception #1 instead of #2.
The exception says that a clock doesn't count against the "only one outlet" requirement. Which says, to me, that an IBC for a fridge can have an extra outlet for a clock and still be an IBC.
And the answer to #2 is apparently a little of both.![]()
Yes, there is. 210.52(B)(1) requires all wall, counter, and refrigeration receptacles to be served by the SABCs. (B)(2) prevents anything else.Mike03a3 said:Since the SA circuits must supply all the receptacles in specified rooms, why do we need an exception for that particular receptacle? There's nothing in the general provisions for receptacles that prevent one from being placed anywhere you might want a clock.
scwirenut said:what if you did actually install a single recept. behind the fridge, (or anywhere for that matter). along comes mr homeowner needing to plug something else up. Will he A: say "oh no, I guess I cant plug up anything else"
or B: get a 3 to 1 adapter and continue plugging away, and if he fills that he will get a multi-strip, and so on and so on. single recepts are a waste of time and money.
scwirenut said:what if you did actually install a single recept. behind the fridge, (or anywhere for that matter). along comes mr homeowner needing to plug something else up. Will he A: say "oh no, I guess I cant plug up anything else"
or B: get a 3 to 1 adapter and continue plugging away, and if he fills that he will get a multi-strip, and so on and so on. single recepts are a waste of time and money.
iwire said:(Bob slamming head against wall) An IBC does not need an exception for more outlets, it only needs an exception for more equipment!!
I can't agree. Look at the definition again:Mike03a3 said:However, I'm also confident that in the specific case of a dwelling, and the use of the exception allowing an individual branch circuit in lieu of supplying a refrigerator with one of the small appliance circuits, an inspector is on solid ground rejecting a duplex receptacle. The inclusion of a second, unused, receptacle, not required for the single permitted utilization equipment (refrigerator), makes it a General-Purpose branch circuit by definition and thus not allowed under the exception.
Not true: A duplex receptacle is two receptacles mounted on one yoke and mounted in one outlet. Remember, a receptacle is only one of several kinds of devices which may be mounted in an outlet.Jim W in Tampa said:If its a duplex it cant be a dedicted single outlet.Duplex is 2 outlets and thats a branch.
tallgirl said:YES, BUT THIS IS THE "CAN I HAVE MORE THAN ONE OUTLET" THREAD.
LarryFine said:I can't agree. Look at the definition again:
"Branch Circuit, Individual. A branch circuit that supplies only one utilization equipment."
Nowhere is there either a requirement for a receptacle nor a requirement that it be a single, as opposed to a duplex, receptacle. It's the act of plugging in a second piece of equipment that changes the characteristics of the outlet.
Not true: A duplex receptacle is two receptacles mounted on one yoke and mounted in one outlet. Remember, a receptacle is only one of several kinds of devices which may be mounted in an outlet.