I was listening to one of those home improvement shows and a question was about the residential refrigerator tripping the circuit breaker. The host said that in the 2008 code, GFCI protection was required. Am I missing something?
Its not a GFCI. It is an LCDI or AFCI. 440.65Im wondering why they started to require gfci on a window a/c unit but not on a frig, they claim the compressor starts to go bad current will leak to ground. the gfci comes on the cord now. A frig or freezer in unfinished basement requires gfci, but that is one code I violate on my own house, a freezer full of rotten food is not a good thing. And it will happen sooner or later with gfci.
Its not a GFCI. It is an LCDI or AFCI. 440.65
Its not a GFCI. It is an LCDI or AFCI. 440.65
shall be provided with factory-installed LCDI or AFCI protection.
What does this have to do with GFCI protection?
Exception #2 to 210.52(B)(1) implies that refrigeration equipment is exempt from GFCI protection.
That's true. Still has nothing to do with requiring GFCI protection of a fridge outlet.
That's the point, it dosen't require it.
There is no need or requirement for a fridge to have a single receptacle.
I would rather have a home owner sue me because there food went bad, rather then sue me because their kid died etc.
Are you saying you wired the signals there?![]()
Actually, though, the NEC is NOT a design guide, it is a minimum set of standards that should be followed.
Anytime you have a receptacle within 6' of a water source you need one 210.8 (7) - handbook narative.
"This change to the code brought GFCI protection to all areas in a dwelling unit in which a sink is installed....it covers all 125 volt 15/20 amp receptacles that are within 6' of any point along the outside edge of the sink."
Also see Exhibit 210.14 in the handbook where it shows a receptacle and a dimension line of 6'-0" to a receptacle.
It also goes on to say that there are NO EXCEPTIONS to this rule.
Would this be close enough sparky?
Anytime you have a receptacle within 6' of a water source you need one 210.8 (7) - handbook narative.
"This change to the code brought GFCI protection to all areas in a dwelling unit in which a sink is installed....it covers all 125 volt 15/20 amp receptacles that are within 6' of any point along the outside edge of the sink."
Also see Exhibit 210.14 in the handbook where it shows a receptacle and a dimension line of 6'-0" to a receptacle.
It also goes on to say that there are NO EXCEPTIONS to this rule.
Would this be close enough sparky?
(6) Kitchens ? where the receptacles are installed to serve the countertop surfaces
(7) Laundry, utility, and wet bar sinks ? where the receptacles are installed within 1.8 m (6 ft) of the outside edge of the sink
For dwellings-
210.8(A):
(6) Kitchens — where the receptacles are installed to serve the countertop surfaces
In a kitchen if it does not serve the countertop surfaces GFCI protection is not required. No mention of sinks or anything except countertops.
Kitchen sinks are not mentioned in this part.(7) Laundry, utility, and wet bar sinks — where the receptacles are installed within 1.8 m (6 ft) of the outside edge of the sink
I agree, part (7) does not apply to a dwelling kitchen sink.
that is for all receptacles, those that serve a counter top and those that don't.
I get calls all the time from electricians ,yelling at us because something is beyond code, they always tell me they didn't install it because it wasn't required. There's nothing I love more when they come to us asking for a letter for something they didn't do that was on the drawings.
Theres so many people out there that take no pride in their work, and miss the whole point of safety issues. The NEC isn't a tax code, where the more you get away with the better.
i'd really like to see a code reference that even comes close to this.