Sorry Steve, I don't understand. The only GFCI devices I know of are 120 and 240 volts for the required receptacles for the maintenance of the HVAC units. Those GFCI units are not very expensive and are very common. :smile:steveng said:what type of GFCI device are available for 480 v 3ph roof units HVAC?
steveng said:what type of gfci device are available for 480 v 3ph roof units hvac?
what is the cost?
thanks,
steve
what is the cost?
thanks,
steve
Its a rec so the HVAC guy doesn't rig up something off the disco for power tools and such.jimday said:Why GFCI for roof top HVAC units? If you are trying to protect an upstream panel or feeder breaker from tripping I would recommend a GFI feeder breaker for the HVAC unit or a GFI relay/protector at the device. Other than that I'm not sure why you would want it.......
210.63 Heating, Air-Conditioning, and Refrigeration Equipment Outlet.
A 125-volt, single-phase, 15- or 20-ampere-rated receptacle outlet shall be installed at an accessible location for the servicing of heating, air-conditioning, and refrigeration equipment. The receptacle shall be located on the same level and within 7.5 m (25 ft) of the heating, air-conditioning, and refrigeration equipment. The receptacle outlet shall not be connected to the load side of the equipment disconnecting means.
Exception: A receptacle outlet shall not be required at one- and two-family dwellings for the service of evaporative coolers.
FPN: See 210.8 for ground-fault circuit-interrupter requirements.
chris kennedy said:Its a rec so the HVAC guy doesn't rig up something off the disco for power tools and such.
I see, OP is looking for protection of a 480 3? RTU. Thats a new one on me. I think OP was asking about the rec.jimday said:I get that there needs to be a GFCI WP maint recept for equipment, but that does not appear to be what was being asked, eh?........
You thinking GFP?Ground-Fault Circuit Interrupter (GFCI). A device intended for the protection of personnel that functions to de-energize a circuit or portion thereof within an established period of time when a current to ground exceeds the values established for a Class A device.
FPN: Class A ground-fault circuit interrupters trip when the current to ground is 6 mA or higher and do not trip when the current to ground is less than 4 mA. For further information, see UL 943, Standard for Ground-Fault Circuit Interrupters.
Ground-Fault Protection of Equipment. A system intended to provide protection of equipment from damaging line-to-ground fault currents by operating to cause a disconnecting means to open all ungrounded conductors of the faulted circuit. This protection is provided at current levels less than those required to protect conductors from damage through the operation of a supply circuit overcurrent device.
chris kennedy said:I see, OP is looking for protection of a 480 3? RTU. Thats a new one on me. I think OP was asking about the rec.
You thinking GFP?