M. D. said:Sorry I try to do the best I can with back up
And you come up with a lot of great stuff
Thanks.
M. D. said:Sorry I try to do the best I can with back up
M. D. said:Are breakers not an option??
M. D. said:Are breakers not an option??
sparky_magoo said:No they're not an option. The ckt. in question is a MWBC.
iwire said:That is not a problem, get two pole GFCIs and be done with it.
sparky_magoo said:I wonder what a GE 2 pole bolt-on brkr. costs. The single pole would have been $111.
sparky-magoo said:The new plan is to have the soda vendor remove the machine. I will then instal a box extender on the existing outlet. I will then pipe around to an exposed GFCI receptacle, and downstream to the existing outlet.
422.51 Cord-and-Plug-Connected Vending Machines.
Cord-and-plug-connected vending machines manufactured
or re-manufactured on or after January 1, 2005, shall include
a ground-fault circuit-interrupter as an integral part of
the attachment plug or be located within 300 mm (12 in.) of
the attachment plug. Older vending machines manufactured
or remanufactured prior to January 1, 2005, shall be connected
to a GFCI-protected outlet. For the purpose of this
section, the term ″vending machine″ means any self-service
device that dispenses products or merchandise without the
necessity of replenishing the device between each vending
operation and designed to require insertion of a coin, paper
currency, token, card, key, or receipt of payment by other
means. [ROP 17-27]
Energize said:A lot cheaper than:
for the whole complex.