A general contractor, trying to save a buck by not using an electrician, installed a new GFCI receptacle in the back yard. He ran the line side wire from this new receptacle back to the interior garage GFCI, attaching it to the load side of the interior GFCI receptacle.
When you test the outside GFCI, it also trips the interior garage GFCI.
He says he does not have to fix it. He wants a code section quoted to him.
I checked under article 110, general workmanship, and I also checked under article 210-8 for Ground fault, and article 300 for general wiring methods. (all from the 2001 California electrical code, which is based on the 1999 NEC.) No luck.
Any help in finding the correct code sectionlisting this as a violation would be appreciated.