can a GFCI replace old work receptacle with no ground wire in bath room.
Highvoltage what you have recommended is a NEC violation and I do not think that is a good idea.Originally posted by highkvoltage:
Personally I would run a #12 if 20 amp or #14 if a 15 amp wire to the cold water line and provide a grounding path.
Highvoltage. What you describe is a violation.Originally posted by highkvoltage:
If I have to install a GFCI where only 2 wires (hot and neutral) were availiable because the wiring was installed many years ago I would install a equipment ground as I suggested. Sometimes you can not apply the newest code to old work and when this occurs I just call the AHJ and proceed from there.
250.130(C) Nongrounding Receptacle Replacement or Branch Circuit Extensions. The equipment grounding conductor of a grounding-type receptacle or a branch-circuit extension shall be permitted to be connected to any of the following:
(1)Any accessible point on the grounding electrode system as described in 250.50
(2)Any accessible point on the grounding electrode conductor
(3)The equipment grounding terminal bar within the enclosure where the branch circuit for the receptacle or branch circuit originates
(4)For grounded systems, the grounded service conductor within the service equipment enclosure
(5)For ungrounded systems, the grounding terminal bar within the service equipment enclosure
I am not saying you have to, but the ground wire you are saying to add is new work.Sometimes you can not apply the newest code to old work