Can anyone cite me a reference that says that receptacles in mechanical room need to be GFCI protected when they are 6' from sink?
Can anyone cite me a reference that says that receptacles in mechanical room need to be GFCI protected when they are 6' from sink?
Rewire, I was just about to type the same thing as you but decided to actually look at the book. Assuming that you are on the 2008 210.8(B)(5) is an addition and reads "Sinks- where receptacles are installed within 1.8m (6 ft) of the outside edge of the sink". There is an exception for industrial laboratories and patient care areas.
Can anyone cite me a reference that says that receptacles in mechanical room need to be GFCI protected when they are 6' from sink?