GFCI location
Rewire, I was just about to type the same thing as you but decided to actually look at the book. Assuming that you are on the 2008 210.8(B)(5) is an addition and reads "Sinks- where receptacles are installed within 1.8m (6 ft) of the outside edge of the sink". There is an exception for industrial laboratories and patient care areas.
We are still on 05 I probably should have mentioned that my bad
Can anyone cite me a reference that says that receptacles in mechanical room need to be GFCI protected when they are 6' from sink?
In NJ - there is no requirement as you describe....we are under the '05 [210.8(B) is the relevant section w/o any amendments]