gfci non trip

Status
Not open for further replies.
Re: gfci non trip

if it is connected right, and there is power applied, and it doesn't trip---it is defective. they say that near 40 per cent of them installed in the field "don't work"!
 
Re: gfci non trip

Don't most "plug-in" GFCI testers require a ground connection? A properly wired GFCI on a 2-wire ungrounded system could not be tested if this is the case.

Most manufacturer literature says the only listed method for testing is the integral Test Button.
 
Re: gfci non trip

Don't most "plug-in" GFCI testers require a ground connection?
I'm going to go out on a limb and guess that they all probably require a ground. Without a ground, they can't create a current imbalance between the neutral and the hot.

Steve
 
Re: gfci non trip

the good old fashioned wiggy from hot to any ground should trip it every time.I had to trouble shoot a gfi once would trip with the test button ,but not with the gfi tester. Result was XO in the transformer was not bonded.
 
Re: gfci non trip

This reminds me of a GFCI tester that I used a few years ago. While holding open the metal weatherproof cover I pressed the test button only to be blasted with 120 volts. Seems that I was kneeling on some damp dirt and the receptacle had no ground. The DIY'er who owned the home decided that the bare ground wire wasn't needed so he simply cut it off at the romex connector.
 
Re: gfci non trip

A ground is not required for a GFI to work properly. Look up the code where you can replace non-grounded outlets with a GFI.

If the outlet is wired properly and does not trip with a "push button" tester, then it is defective.
Leviton just had a bunch that where defective.

Check with your supplier. But again, a grounded conductor is not required for the GFI to work properly.
 
Re: gfci non trip

The test button on the GFCI creates a ground fault internally hot to neutral and trips the GFCI. The GFCI external tester tests hot to equipment ground, if it does not trip then the equipment ground is missing or incomplete.
The mfgs recommended method is to use the GFCI test button
 
Re: gfci non trip

for tom baker . why would the equipment ground have anything to do with the trip when the trip is done by shorting the hot and neutral? I did not use a tester on these only the test button on the gfi. These are leviton devices and one of them tripped once and then would not repeat. The second would not trip at all. Havent ried a third one yet but this is the first tiem thie has ever happened to me in the field.2 out of 2 bad? please expand on why you feel the egc has anything at all to do with the trip test as an egec is not required for a gfci to operate.
 
Re: gfci non trip

Stew If the GFCI didn't trip by the trip button on the unit or can not be reset after triping the unit it either has the feed conductors connected to the load terminals which can only happen on older GFCI's (Non-fail safe) or on newer ones which has had the reset button reset then the feed wires switched to the load side. Or flat out you got a bad lot of GFCI's.

If you look at the two diagrams of a GFCI circuit below, you can see how the test button places a 5ma load from the load side hot to the line side neutral which will act just like a ground fault. If these GFCI's are used to replace receptacles on a non-gounded circuit they will still funtion but a plug in tester will not be able to test them as they require a grounding source to "leak" the current to, to cause the imbalance to trip it.

wpe1.gif


This diagram shows the fault current which trips the GFCI.
wpe2.gif
 
Re: gfci non trip

Bigjohn67,
But again, a grounded conductor is not required for the GFI to work properly.
Really?? I think that you meant to say "grounding conductor". If so you are correct that the GFCI will function correctly without an EGC, but in that case you can't use a plug-in tester to test it. See the diagram posted by Wayne.
Don
 
Re: gfci non trip

You may have an old GFCI. A word of caution back in the mid 1980's, my associate and I got a call about a GFCI receptacle not tripping. We tried some different wiring screw-ups. We connected the supply conductors to the load-side of the GFCI, guess what, it didn't trip. UL then changed the internal wiring so that the GFCI would not energize if the it was wire incorrectly.
 
Re: gfci non trip

Do any of you use the Ideal "Sure Test". I bought mine to try and explain voltage drops to home inspectors. It seems to work well for finding sneaky little problems. Poor connections, neutral to ground( arc fault breaker problems), bootleg grounds. I find I can check a house quickly with it and if I find a problem I get the meter out.Just thought I would mention it. Looks like a toy but works great. Buy the way I got a bunch of those bad Leviton GFCI's and some bad Leviton switches. I have pretty much switched brands now.
I think they should have some sort of quality controll. It's embarrassing in the field to install products that don't work.
 