I'm doing some work on a ranch where there was a service feeding a mobile home via a 50a fused disconnect. At some point someone tapped off of a single line on the load side of the disconnect, and ran it, along with a neutral conductor, underground to a bunk house.
In the bunkhouse there was a small panel and the single hot was ran to both L1 and L2, and there were some single pole breakers installed feeding a few circuits in the bunkhouse.
I installed a new service panel, with a 50a breaker feeding the mobile home, and planned to run a 50a 2-pole circuit over to the bunkhouse and install a new sub-panel. Of course its never simple, the conduit going underground was simply 90ed and then the two conductors were direct buried. That has delayed the pulling of the new feeders.
Anyway, I got the new sub panel installed and ran new circuits for a fridge, and a 120v hot water heater. There was some other troubleshooting to do in the bunkhouse so I temporarily energized the panel to see if I could make use of the time I was there to do that. I wanted to test the new GFCI's first and with no other circuits on I energized the two dedicated circuits that I had just ran. The GFCI's would not reset. I knew that the ground was open but also that GFCIs don't need one to function so I had to scratch my head a bit.
Out of curiosity I installed the bonding screw in the sub panel, where the neutral had previously been isolated, and the ground installed on the can, but was really just floating. After that, the GFCIs would reset and function properly.
Im kind of at a loss on this. I know there may be other wiring issues in the bunkhouse given how work was done previously, but I don't understand how the new circuits I had just ran directly from sub-panel to GFCI would be affected by those issues, given that no other circuits were energized.
Didn't have a lot of time to try to figure that out but I am gonna see what happens once I get the new feeders installed. For now I just wanted to run it by the forum and see if there is something I am missing or should have checked.
Thanks
In the bunkhouse there was a small panel and the single hot was ran to both L1 and L2, and there were some single pole breakers installed feeding a few circuits in the bunkhouse.
I installed a new service panel, with a 50a breaker feeding the mobile home, and planned to run a 50a 2-pole circuit over to the bunkhouse and install a new sub-panel. Of course its never simple, the conduit going underground was simply 90ed and then the two conductors were direct buried. That has delayed the pulling of the new feeders.
Anyway, I got the new sub panel installed and ran new circuits for a fridge, and a 120v hot water heater. There was some other troubleshooting to do in the bunkhouse so I temporarily energized the panel to see if I could make use of the time I was there to do that. I wanted to test the new GFCI's first and with no other circuits on I energized the two dedicated circuits that I had just ran. The GFCI's would not reset. I knew that the ground was open but also that GFCIs don't need one to function so I had to scratch my head a bit.
Out of curiosity I installed the bonding screw in the sub panel, where the neutral had previously been isolated, and the ground installed on the can, but was really just floating. After that, the GFCIs would reset and function properly.
Im kind of at a loss on this. I know there may be other wiring issues in the bunkhouse given how work was done previously, but I don't understand how the new circuits I had just ran directly from sub-panel to GFCI would be affected by those issues, given that no other circuits were energized.
Didn't have a lot of time to try to figure that out but I am gonna see what happens once I get the new feeders installed. For now I just wanted to run it by the forum and see if there is something I am missing or should have checked.