GFCI on 4 wire dryer outlet what is the reference?

Status
Not open for further replies.

phantomniceguy

New member
Is it required to have a gfci on a 4 wire dryer outlet? I see the NEC reference saying that all new install shall be 4 wire type with neutral and ground but the GFCI section references only 125 VAC not 250 VAC. All our dryers on the base are within 6 feet of sinks so our safety office is writing them up for GFCI but I need the actual reference to complete the upgrade or it will not happen. Any inputs greatly appreciated.
 

tom baker

First Chief Moderator
Staff member
GFCI is not required for 240 V receptacles in dwelling units. Perhaps your safety office needs to understand the purpose of GFCIs is to protect those using portable electrical devices plugged into receptacles from shock. There is not the same exposure with a dryer.
 

gar

Senior Member
Location
Ann Arbor, Michigan
Occupation
EE
091002-1534 EST

If you use a GFCI on a dryer and there is a failure of the EGC you will be providing good protection. If the dryer is inferior and has leakage current to the cabinet, then the GFCI with a good EGC will detect the defective dryer.

The NEC is a minimum, nothing wrong with doing a better job. If there are nuisance trips, then the cause needs to be determined.

For a high reliability system redundancy is an important tool.

.
 