GFCI on a 12/3?

Status
Not open for further replies.
Re: GFCI on a 12/3?

Originally posted by infinity:
Would sharing the neutral between one SA circuit and one Non-SA circuit be a violation?
No, why do you think that it would?
WEll, 210.52(B)(2) says ...the circuits shall have no other outlets.

The neutral is a major part of the circuit!

so, Since the neutral is part of the circuit, and the circuit can't have any other outlets, the neutral can't have any other outlets.

I don't like it, but I can't find an exception to allow it.

Dave
 
Re: GFCI on a 12/3?

Originally posted by davedottcom:
Originally posted by infinity:
Would sharing the neutral between one SA circuit and one Non-SA circuit be a violation?
No, why do you think that it would?
WEll, 210.52(B)(2) says ...the circuits shall have no other outlets.

The neutral is a major part of the circuit!

so, Since the neutral is part of the circuit, and the circuit can't have any other outlets, the neutral can't have any other outlets.

I don't like it, but I can't find an exception to allow it.

Dave
Same goes for Bath GFCI's. 210.11(C)(3) says ...circuit shall have no other outlets.

Same for Laundry.

Unless the neutral isn't considered part of the circuit!?

Dave
 
Re: GFCI on a 12/3?

210.4(A) allows a shared neutral circuit to be considered to be multiple circuits. An SA circuit and a nonSA circuit can share the same neutral but CANNOT have phase to phase load.

At one time Mahoning County ( where Youngstown, Ohio is ) had a requirement that each receptacle location in a kitchen had to have 240 volts available in case somebody needed to plug in a 240 volt medium size appliance. Medium sized applicances appliances never materialized. I have seen a duplex receptacle that was both a duplex 120 volt receptacle and a DUPLEX 240 volt receptacle. Each half of the receptacle had 4 slots - 2 parallel and 2 tandem. Old houses have the strangest things.
 
Re: GFCI on a 12/3?

Originally posted by mc5w:
210.4(A) allows a shared neutral circuit to be considered to be multiple circuits. An SA circuit and a nonSA circuit can share the same neutral but CANNOT have phase to phase load.
mc5w,you might want to look code sections up rather than shooting from the hip. :D

A multiwire branch circuit may feed both line to line and line to neutral loads.

MWBC.JPG


You could, if you wanted to, wire a circuit as pictured above.

210.4(C) Line-to-Neutral Loads. Multiwire branch circuits shall supply only line-to-neutral loads.

Exception No. 1: A multiwire branch circuit that supplies only one utilization equipment.

Exception No. 2: Where all ungrounded conductors of the multiwire branch circuit are opened simultaneously by the branch-circuit overcurrent device.
 
Re: GFCI on a 12/3?

Originally posted by mc5w:
210.4(A) allows a shared neutral circuit to be considered to be multiple circuits. An SA circuit and a nonSA circuit can share the same neutral...
Thanks Mc5w!

I can't believe I kept missing that!? :(

Dave

Has this site's "speed" really slowed down lately or is it my new PC?
 
Re: GFCI on a 12/3?

Dave, it's real slow here this morning. Maybe something to do with activity associated with the storm.

Roger
 
Re: GFCI on a 12/3?

Originally posted by davedottcom:
WEll, 210.52(B)(2) says ...the circuits shall have no other outlets.

The neutral is a major part of the circuit!

so, Since the neutral is part of the circuit, and the circuit can't have any other outlets, the neutral can't have any other outlets.

I don't like it, but I can't find an exception to allow it.

Dave
Sometimes you guys amaze me with the stuff you come up with. :eek:
 
Re: GFCI on a 12/3?

Originally posted by electricmanscott:
Sometimes you guys amaze me with the stuff you come up with. :D

Apparently someone else (Who ever wrote 210.4(A) thought of it long before I did.
:p

Dave
 
Status
Not open for further replies.
Top