Re: GFCI on load side of AFCI?
Just for the heck of it I just set up the eq. circuit up on my electrical bench.
I used a GE single pole 20 amp.#THQL1120AFP AFCI and a 15 amp. recpt. 20 amp. feed through GFI receptacle # XGF15V-SP ShockSentry made by Cooper.
Didn't take any current readings but I used a Ideal solenoid wiggy tester and a test light with a 60 watt 120 volt incandescent light bulb.
Well heres what happen.
1.-With wiggy tested between the hot and neutral on AFCI 120 vac.
2.-With wiggy tested between the hot and neutral on GFI 120 vac.
3.-Pushed test button on AFCI, AFCI trips as should.
4.-Pushed built in test on GFI, GFI trips no effect on AFCI did not trip.
Now this fooled me like I said I didn't take any current measurements.
5.-Touched one wiggy probe to hot on GFI load side and the other one to the eq. ground on the GFI,GFI tripped had no effect on the AFCI held did not trip.
6.-Touched one wiggy probe to the hot load side of the AFCI breaker and the other wiggy probe to the eq. ground on the AFCI held did not trip the AFCI like I thought it would.The wiggy coils impedance is not low enough to allow enough current to flow to trip the AFCI breaker.
Now I used the light bulb tester for more current.
7.-Touched one probe of the bulb tester to the GFI hot load side and the other one to the GFI ground terminal, did this four times reseting the devices each time, First time just the AFCI kicked next three time both the AFCI breaker and the GFI recpt. tripped.It was a horse race.
I don't have a problem using them together now.
I think its a dependable combination.
Just thought I'd pass this information on might not help but sure can't hurt.
The only thing that has me puzzled now is like I said on one house inspection I had the electrical inspectors wiggy to kick my AFCI circuit when he went from the GFIs recpt. hot to ground.
His wiggy either pulled more current than my or it might have been since the run was longer than my bench circuit maybe the circuit capacitance made the difference?
Ronald