The rod to earth resistance is nearly always too high to give a reliable path to facilitate operation of overcurrent devices or even to carry normal circuit loading. 10 ohms would be considered a good ground rod install, yet it will limit a 120 volt fault to 12 amps - never going to trip a 15 amp breaker.That's an interesting point... Do you mean that in the sense that it can provide a return path to the source and actually create a path for the unbalanced current to flow? Seems though to a certain degree this would provide a more "reliable" path for the unbalanced current than the current that would otherwise flow from capacitive charging.
This is all interesting to me. Bonding is critical to have a low-resistance path to the source to clear ground-faults on grounded systems. We want high levels of current to flow to trip breakers. But now it seems grounding, though it does nothing to trip a breaker on a fault, could be beneficial to trip a GFCI considering the little bit of current it requires... Granted choosing a grounded system solely for this reason is unlikely.
Which leads me to this...
By what standard? NEC? Or are you saying only recognized as such by the manufacturer?
GFCI - it certainly will make them trip almost immediately in most cases of "ground fault" if you have a grounded system.
If you don't have a grounded system - you need a second ground fault or there is no fault current, but remember the purpose of GFCI is preventing electrocution - there is no shock hazard on first ground fault in an ungrounded system - all that first fault does is establish a ground reference to the system.