- Tennessee NEC:2017
- Semi-Retired Electrician
WARNING.....Very long post. Sorry, I don't know how to explain it other than make it a novel!
I got a call from a customer saying his GFCI breaker is tripping. It is a 120V 20A Siemens GFCI.
Here is what is on the circuit:
Post light with a photo cell
Small pump for a fountain that is plugged in but not running or even turned on.
250W metal halide 120V yard light on a photo cell
Dehumidifier under the house with a cord cap to a duplex recep.
Condensate pump for the dehumidifier
Here is the details concerning when it trips, it doesn't trip immediately:
Post light & yard light come on but don't know which comes on first, dehumidifier is on all the time as well as the condensate pump. The small fountain pump is plugged in but not turned on. Anywhere from 45 mins to 1 hour after the lights come on it trips.
This is what I have done so far but it still trips.
Covered the PC for the post light to allow the light to come on. Let it stay on about 15 minuites.
Disconnected the yard light at the junction box on the pole. The junction box also has a GFCI receptacle in it. I left the GFCI recep and just disconnected the feed to the light/photo cell. Left for the night. Customer called back the next morning saying it still tripped.
Went back today and took the post light off the pole. Checked the connections, sockets, etc. I checked for continuity between hot-ground, neutral ground all good. I decided to go a step farther and checked the light with a megger. That also checked good.
Went under the house and disconnected the feed (UF) wire where it was connected in a junction box. Went back out and meggered the UF with nothing connected at either end.
That checked good with the megger. Connected the feed back in the junction box. Put a pigtail w/lamp socket instead of the post light and let it stay on about 1/2 hour with no trip.
Now I don't know how to check a PC other than to see if it's switching or not so I just changed the PC. Put the light back on the post. The reason I changed the PC is the customer had taped up the eye earlier in the morning to see if it would come on. That's when he said it stayed on for about an hour then tripped. He said the breaker would not reset and that's when he called me. I told him to remove the tape and see if it would reset, which it did. He also said he went under the house and turned the dehumidifier to where it would run. It ran with nothing else running and the breaker held. So I thought I would just eliminate the possibility of a bad PC.
Went back to the yard light and removed the GFCI receptacle & replaced with just a regular duplex since the circuit was already on a GFCI breaker. Connected the yard light back. It came on as soon as the breaker was reset. I think the PC does that when first powered up after the power has been disconnected. It stayed on for about a minute then went off, breaker not tripped. Post light came on and stayed on because I had tape over the eye. I watched the post light for a while and told the customer to leave the tape on until dark then pull it off. I left but told him to let me know if it held. He called me about an hour later and said it tripped again.
I just told him to try one more thing with the post light. I told him to change the bulbs and see if that helps. So I haven't heard back but that doesn't mean anything as he may be waiting to call tomorrow.
I'm confused as to why the breaker only trips when the post light is on but then only after a while. If the dehumidifier is the problem, why doesn't it trip during the day?
I'm sure it has to come on some during the day.
Since the fountain pump hasn't been on during any of the tripping I don't think it is the problem.
Anyone have any suggestions? I may have left something out, so ask away if it seems I left out anything.