Would the receptacles on the customer side of a bar in a restaurant be required to be GFCI protected? These are generally located below the bar top for customers to plug in their phones.
...I recently bid a project that showed a 50 amp 120v receptacle in a commercial kitchen. My supplier said GE or anyone else that they knew of does not make a 1/50 GFCI breaker or receptacle. How do you satisfy this requirement?
How often do you run into a 50 amp 120 volt receptacle? Even if you did have the need just use one pole and neutral off a two pole (GFCI) breaker.Damn. Thought I had all of the info down. I knew what I was describing in my head.:dunce:
Assume there is a sink on the server side of the bar.
Also, 210.8(B) states that all single phase receptacles 150v to ground or less, 50 amps or less..... are required to be GFCI protected. I recently bid a project that showed a 50 amp 120v receptacle in a commercial kitchen. My supplier said GE or anyone else that they knew of does not make a 1/50 GFCI breaker or receptacle. How do you satisfy this requirement?
Would the receptacles on the customer side of a bar in a restaurant be required to be GFCI protected? These are generally located below the bar top for customers to plug in their phones.
No, unless they are within 6 feet of a sink.
210.8(B)(5).
:thumbsdown::slaphead:Nope.
See 210.8(B)
Damn. Thought I had all of the info down. I knew what I was describing in my head.:dunce:
Assume there is a sink on the server side of the bar.
Also, 210.8(B) states that all single phase receptacles 150v to ground or less, 50 amps or less..... are required to be GFCI protected. I recently bid a project that showed a 50 amp 120v receptacle in a commercial kitchen. My supplier said GE or anyone else that they knew of does not make a 1/50 GFCI breaker or receptacle. How do you satisfy this requirement?
:thumbsup:
:thumbsdown::slaphead:
They do have 50a gfci dp brkrs- just do as kwired said
And yes, a 120v 50a rec does indeed exist-----a NEMA "5-50"- just picture a "king size" standard grounding type rec- that is seriously what the thing looks like.
What in the heck are they planning on plugging in? Are you sure this is what they spec'd?
How much does that one circuit throw off load balance of your panel?@ Kwired
Unless the Panel is full. No space for 2/50.
Lol. Getting off topic. The original question was "How do you satisfy the requirements of a GFCI protected receptacle of 120v up to 50amps?" Since there doesn't seem to be a manufacturer of a 1/50 GFCI breaker of any brand.