For clarification, all of the following is considered to be inside a dwelling unit.
I know this has been kicked around before, but I haven't seen any clear stance from the NFPA on this issue. I know some municipalities use a "cord path" type length and that passing through a door (including cabinet door) negates the need for GFCI protection.
With that said it is my understanding that in past commentary 210.8(A)7 was intended for GFCI protection of receptacles within 6 ft of all OTHER sinks (indicating that it did not apply in the kitchen). That wording is not there. Is the receptacle under the sink "within 1.8 (6 ft) of the outside edge of the sink" in terms of needing GFCI protection? Is this an all encompassing measurement for each level of the home (stopping at the floor/ceiling) or a straight line distance from the edge? If it is a cord-connected path distance, does the measurement stop when it encounters a cabinet door?
Also for clarification, I get argued time and time again that laundry room washing machine receptacles are not required to be GFCI protected unless they are within 6ft of a sink. My understanding is that 210.8(A)(10) includes the washing machine receptacle, AND it must be accessible (not blocked).
Thanks for any insight.
I know this has been kicked around before, but I haven't seen any clear stance from the NFPA on this issue. I know some municipalities use a "cord path" type length and that passing through a door (including cabinet door) negates the need for GFCI protection.
With that said it is my understanding that in past commentary 210.8(A)7 was intended for GFCI protection of receptacles within 6 ft of all OTHER sinks (indicating that it did not apply in the kitchen). That wording is not there. Is the receptacle under the sink "within 1.8 (6 ft) of the outside edge of the sink" in terms of needing GFCI protection? Is this an all encompassing measurement for each level of the home (stopping at the floor/ceiling) or a straight line distance from the edge? If it is a cord-connected path distance, does the measurement stop when it encounters a cabinet door?
Also for clarification, I get argued time and time again that laundry room washing machine receptacles are not required to be GFCI protected unless they are within 6ft of a sink. My understanding is that 210.8(A)(10) includes the washing machine receptacle, AND it must be accessible (not blocked).
Thanks for any insight.