210.8 (A) (5)- Unfinished basements: For purposes of this section, unfinished basements are defined as portions or areas of the basement not intended as habitable rooms and limited to storage areas, work areas, and the like.
Exception No. 1 to (5) - Receptacles that are not readily accessible.
Exception No. 2 to (5) - A single receptacle or a duplex receptacle for two appliances located within dedicated space for each appliance that, in normal use, is not easily moved from one place to another and that is cord-and-plug connected in accordance with 400.7 (A)(6), (A)7, or (A)(8).
Exception No. 3 to (5) - A receptacle supplying only a permanently installed fire alarm or burglar alarm system shall not be required to have ground-fault circuit-interrupter protection. Receptacles installed under the exceptions to 210.8 (A)(5) shall not be considered as meeting the requirements of 210.52 (G)."