GFCI protection

Location
Maryland
Occupation
Electrician
So I just had a kitchen final inspection and the inspector said that the kitchen circuits could not have an arc breaker / gfci outlet combination. He said it needs to be a dual function breaker so that the whole circuit is gfi protected. Is that correct. The area is on the 2023 code.
 
I think one of the few places in the code for complete branch circuit GFCI protection was swimming pool lights. Everything else seems to be outlet or receptacle protection only.
 
So I just had a kitchen final inspection and the inspector said that the kitchen circuits could not have an arc breaker / gfci outlet combination. He said it needs to be a dual function breaker so that the whole circuit is gfi protected. Is that correct. The area is on the 2023 code.
Inspector is wrong! Unless there is a local amendment.

Ron
 
I agree with the others but I recall there was a recent change that says GFCI's need to be readily accessible? that in some cases like a dishwasher makes a breaker with GFCI a common choice.
 