I was asking Rob, whether it was a local requirement like on a outside single recep. for a pool. I know all singles don't have to be twist lock. But thanks for your input.
You're welcome!
I was asking Rob, whether it was a local requirement like on a outside single recep. for a pool. I know all singles don't have to be twist lock. But thanks for your input.
I was asking Rob, whether it was a local requirement like on a outside single recep. for a pool. I know all singles don't have to be twist lock. But thanks for your input.
I am wiring an addition, and in the laundry room there is a sink right beside a stackable washer/dryer, a 220 volt 20 amp 4-wire for the dryer and a 120 volt 20 amp circuit for each washer, there is also a undercabinet light that is being installed right above the sink, since all these items are going to be extremely close to the sink do any of these need to be gfci protected?
I agree, unless there is a local code. Here in NJ we can still use single devices in lieu of GFCI's.
I was only referring to the question given in the OP:
The exception to dedicated space receptacles was removed in 2008, some areas of the country that are still on the 2005 NEC can still use it.
We're under the 2008 but a local State amendment still allows the use of non-GFCI protected single receptacles in the dedicated spaces that Hurk mentioned. Basically they have kept the 2005 exception intact.
This is from the UCC and does not alter 2008 NEC 210.8 a (7) which deals with laundry sinks. So even in NJ they would need to be GFI protected. Twist lock receptacles are not required to meet the exceptions.