We recently received a red tag for these items in a single family dwelling and I cannot find in the NEC where he is getting this from. Can anyone point to the NEC article that states?...
1. All GFCI protected outlets must have a GFCI label attached to the outlet.
I understand this to be true when using GFCI outlets, all other outlets downstream must be labeled as such. However in this case, the GFCI protection is provided by a dual function GFCI/AFCI breaker. When that is the case, my understanding is you do not need labels on the outlets.
2. All bathrooms and the outlet used for servicing the AC condenser (within 25') must be resettable GFCI outlets.
Again, these outlets are protected by duel function GFCI/AFCI breakers. I understand for convenience sake this is true but where in the NEC is this stated?
We use duel function breakers on every circuit in the panel for years and have never had an inspector call us out on these things.
1. All GFCI protected outlets must have a GFCI label attached to the outlet.
I understand this to be true when using GFCI outlets, all other outlets downstream must be labeled as such. However in this case, the GFCI protection is provided by a dual function GFCI/AFCI breaker. When that is the case, my understanding is you do not need labels on the outlets.
2. All bathrooms and the outlet used for servicing the AC condenser (within 25') must be resettable GFCI outlets.
Again, these outlets are protected by duel function GFCI/AFCI breakers. I understand for convenience sake this is true but where in the NEC is this stated?
We use duel function breakers on every circuit in the panel for years and have never had an inspector call us out on these things.