GFCI rec

Status
Not open for further replies.

hhuzzel

Member
Location
NJ
Can anyone tell me how many duplex rec can be protected from one GFCI and does the code have any Articles that tell me this?
 
Thanks for your answer but some inspectors have failed me for puting more than five where are they getting their information :?
 
Have you asked them to cite you a code they may be using?

Roger
 
hhuzzel,

On the outside chance, is it possible that this is a local ordinance? Rule that out.

Save the manufacturer's instruction sheet for the GFCI that you install. When the inspector brings it up, show him, fax him, email him, whatever, the full sheet and ask for where the "five count" limit is stated.

The UL General Information for Electrical Equipment Directory (the so-called "White Book") does not state a limit, nor is it any where in the NEC.
 
I asked a manufacturer's tech support group if they had a limit on the number of ordinary duplex receptacles that could be protected on the load side of one of their GFCIs.

Their reply: Up to 9 receptacles from a branch circuit can be put on a GFCI, however your local laws dictate how many you allowed to be put. [sic]

Mike
 