A GFCI has two torroid coils or CTs. One detects the current imbalance between hot and neutral, the other detects the grounded netural, as you can get a shock from the neutral. The grounded neutral CT is what trips the GFCI on a neutral to ground connection, and by the way we have the same protection in an AFCI, but at higher trip level. Thus a common reason for AFCI tripping is a neutal to ground connection.