Re: GFCI required locations
The code says that in the kitchen, or at a wet bar sink, the receptacles intended to serve the countertop are required to have GFCI protection for personnel. The receptacle you are describing is not in the kitchen. Therefore, the requirement does not apply. You are welcome to add GFCI protection if you like, and are willing to pay for it, but the NEC does not require it.
Reference: NEC 210.8(A)(6) and (7).