A GFCI is required on outside of single family dwelling for 120V corded sump pump based on 210.8 (A)(3), no exceptions correct? I know I'm beating a dead horse with this one, but I might have to go through litigation so I want to be sure. He wanted me to install a regular receptacle for the pump, but I refused because not only is it against code, but I didn't/don't want to be responsible for electrocuting anyone! So of course the GFCI tripped and the basement flooded. I tried to tell him that the pump had to have caused the GFCI to trip, and since I didn't provide the pump, I'm not responsible for the floor. But the GC keeps trying to bring up 620.85, and I keep telling him that the article he is reciting is for Elevators, Dumbwaiters, Escalators, Moving Walks, Platform Lifts, and Stairway Chairlifts ONLY. What are your guys thoughts in this whole matter? Thanks...
ARTICLE 620
Elevators, Dumbwaiters, Escalators,
Moving Walks, Platform Lifts, and
Stairway Chairlifts
620.1 Scope. This article covers the installation of electrical
equipment and wiring used in connection with elevators,
dumbwaiters, escalators, moving walks, platform lifts,
and stairway chairlifts.
620.85 Ground-Fault Circuit-Interrupter Protection for
Personnel. Each 125-volt, single-phase, 15- and 20-ampere
receptacle installed in pits, in hoistways, on elevator car
tops, and in escalator and moving walk wellways shall be
of the ground-fault circuit-interrupter type.
All 125-volt, single-phase, 15- and 20-ampere receptacles
installed in machine rooms and machinery spaces
shall have ground-fault circuit-interrupter protection for
personnel.
A single receptacle supplying a permanently installed
sump pump shall not require ground-fault circuit interrupter
protection.
For reference:
210.8 Ground-Fault Circuit-Interrupter Protection for
Personnel. Ground-fault circuit-interrupter protection for
personnel shall be provided as required in 210.8(A) through
(D). The ground-fault circuit-interrupter shall be installed in
a readily accessible location.
Informational Note: See 215.9 for ground-fault circuit interrupter
protection for personnel on feeders.
(A) Dwelling Units. All 125-volt, single-phase, 15- and
20-ampere receptacles installed in the locations specified in
210.8(A)(1) through (10) shall have ground-fault circuit interrupter
protection for personnel.
(1) Bathrooms
(2) Garages, and also accessory buildings that have a
floor located at or below grade level not intended as
habitable rooms and limited to storage areas, work
areas, and areas of similar use
(3) Outdoors
Exception to (3): Receptacles that are not readily accessible
and are supplied by a branch circuit dedicated to
electric snow-melting, deicing, or pipeline and vessel heating
equipment shall be permitted to be installed in accordance
with 426.28 or 427.22, as applicable.
(4) Crawl spaces — at or below grade level
(5) Unfinished basements — for purposes of this section,
unfinished basements are defined as portions or areas
of the basement not intended as habitable rooms and
limited to storage areas, work areas, and the like
Exception to (5): A receptacle supplying only a permanently
installed fire alarm or burglar alarm system shall
not be required to have ground-fault circuit-interrupter
protection.
Informational Note: See 760.41(B) and 760.121(B) for
power supply requirements for fire alarm systems.
Receptacles installed under the exception to
210.8(A)(5) shall not be considered as meeting the
requirements of 210.52(G)
(6) Kitchens — where the receptacles are installed to
serve the countertop surfaces
(7) Sinks — where receptacles are installed within 1.8 m
(6 ft) of the outside edge of the sink
(8) Boathouses
(9) Bathtubs or shower stalls — where receptacles are
installed within 1.8 m (6 ft) of the outside edge of the
bathtub or shower stall
(10) Laundry areas
ARTICLE 620
Elevators, Dumbwaiters, Escalators,
Moving Walks, Platform Lifts, and
Stairway Chairlifts
620.1 Scope. This article covers the installation of electrical
equipment and wiring used in connection with elevators,
dumbwaiters, escalators, moving walks, platform lifts,
and stairway chairlifts.
620.85 Ground-Fault Circuit-Interrupter Protection for
Personnel. Each 125-volt, single-phase, 15- and 20-ampere
receptacle installed in pits, in hoistways, on elevator car
tops, and in escalator and moving walk wellways shall be
of the ground-fault circuit-interrupter type.
All 125-volt, single-phase, 15- and 20-ampere receptacles
installed in machine rooms and machinery spaces
shall have ground-fault circuit-interrupter protection for
personnel.
A single receptacle supplying a permanently installed
sump pump shall not require ground-fault circuit interrupter
protection.
For reference:
210.8 Ground-Fault Circuit-Interrupter Protection for
Personnel. Ground-fault circuit-interrupter protection for
personnel shall be provided as required in 210.8(A) through
(D). The ground-fault circuit-interrupter shall be installed in
a readily accessible location.
Informational Note: See 215.9 for ground-fault circuit interrupter
protection for personnel on feeders.
(A) Dwelling Units. All 125-volt, single-phase, 15- and
20-ampere receptacles installed in the locations specified in
210.8(A)(1) through (10) shall have ground-fault circuit interrupter
protection for personnel.
(1) Bathrooms
(2) Garages, and also accessory buildings that have a
floor located at or below grade level not intended as
habitable rooms and limited to storage areas, work
areas, and areas of similar use
(3) Outdoors
Exception to (3): Receptacles that are not readily accessible
and are supplied by a branch circuit dedicated to
electric snow-melting, deicing, or pipeline and vessel heating
equipment shall be permitted to be installed in accordance
with 426.28 or 427.22, as applicable.
(4) Crawl spaces — at or below grade level
(5) Unfinished basements — for purposes of this section,
unfinished basements are defined as portions or areas
of the basement not intended as habitable rooms and
limited to storage areas, work areas, and the like
Exception to (5): A receptacle supplying only a permanently
installed fire alarm or burglar alarm system shall
not be required to have ground-fault circuit-interrupter
protection.
Informational Note: See 760.41(B) and 760.121(B) for
power supply requirements for fire alarm systems.
Receptacles installed under the exception to
210.8(A)(5) shall not be considered as meeting the
requirements of 210.52(G)
(6) Kitchens — where the receptacles are installed to
serve the countertop surfaces
(7) Sinks — where receptacles are installed within 1.8 m
(6 ft) of the outside edge of the sink
(8) Boathouses
(9) Bathtubs or shower stalls — where receptacles are
installed within 1.8 m (6 ft) of the outside edge of the
bathtub or shower stall
(10) Laundry areas