GFCI requirements for water coolers
IHer
New member
Can someone tell me if a GFCI is required for a portable water cooler? The OSHA standard 1910.305(j)(2)(IV) is vague and states a receptable installed in a wet or damp location shall be suitable for the location. the compliance officer will usually reference a NEC code (i believe 210) to back their citation. is there a NEC code pertaining to GFCI for water coolers? why wouldnt a GFCI be required for a water cooler?
Welcome to the forum.:)
The NEC does require GFCI protection of drinking fountains but not portable water coolers unless the receptacle is located in an area specified in 210.8. Here is what 422.52 says;
422.52 Electric Drinking Fountains. Electric drinking fountains
shall be protected with ground-fault circuit-interrupter
protection.
Chris
There was little substantion when GFCI's were required for drinking fountains, which I belive was the 08 NEC.\
A water cooler is not much different than a water heater, both have water in contact with heating elements.
I don't see the danger for either.