stuartdmc
Senior Member
- Location
- Newport Beach, Irvine, CA
I currently designed a restaurant in Laguna Beach CA which the electrical plan checker has corrected me on a GFCI issue, I meet with him today however, he is demanding to enforce section 210.8(b) and says that ?ALL? receptacles in the kitchen needs to be GFCI protected. I have engineered a lot of restaurants in the past and never have I had to GFCI protect a dedicated 125V 20A receptacles circuits. He asked me to provide him documentation otherwise.
I haven?t really looked yet, but would section 220.20 apply?
Thanks for your help..
Stu.