GFCI?s in a Commercial kitchen ?

Status
Not open for further replies.

stuartdmc

Senior Member
I currently designed a restaurant in Laguna Beach CA which the electrical plan checker has corrected me on a GFCI issue, I meet with him today however, he is demanding to enforce section 210.8(b) and says that ?ALL? receptacles in the kitchen needs to be GFCI protected. I have engineered a lot of restaurants in the past and never have I had to GFCI protect a dedicated 125V 20A receptacles circuits. He asked me to provide him documentation otherwise.
I haven?t really looked yet, but would section 220.20 apply?
Thanks for your help..
Stu.
 
stuartdmc said:
I currently designed a restaurant in Laguna Beach CA which the electrical plan checker has corrected me on a GFCI issue, I meet with him today however, he is demanding to enforce section 210.8(b) and says that ?ALL? receptacles in the kitchen needs to be GFCI protected. I have engineered a lot of restaurants in the past and never have I had to GFCI protect a dedicated 125V 20A receptacles circuits. He asked me to provide him documentation otherwise.
I haven?t really looked yet, but would section 220.20 apply?
Thanks for your help..
Stu.

I am afraid your plan checker is correct. Make sure the gfci is in an accessible place or as a breaker in the panel.
 
stuartdmc said:
I was thinking of 2002 NEC 220.20 Kitchen Equipment?

I can’t believe that all circuit, even the 110V circuits for the equipment under the hood which are all on a shunt trip have to be on a GFCI.


I think it makes sense, commercial kitchens tend to have water standing on the floor constantly, and its a pretty common practice for workers to spray down walls to clean, not to mention that kitchen equipment tends to have damaged insulation on the cords.

edit- Its only the 20 amp 120v circuits that are required to be GFCI protected
 
stuartdmc said:
I was thinking of 2002 NEC 220.20 Kitchen Equipment?

I can?t believe that all circuit, even the 110V circuits for the equipment under the hood which are all on a shunt trip have to be on a GFCI.

It is a fact, the requirement is due to electrocutions in commercial kitchens, you can see this substantiation in reviewing the ROP's.

Roger
 
stuartdmc said:
I was thinking of 2002 NEC 220.20 Kitchen Equipment?

I can?t believe that all circuit, even the 110V circuits for the equipment under the hood which are all on a shunt trip have to be on a GFCI.

Well, it changed in 2005-- If you are still under the 2002 then you may be okay. I don't have a 2002.
 
Ok. I see your point. What year code change was that?

What if I where to hard wire the piece of equipment, would it still need the protection? The panels that are feeding the equipment are within 25ft so I wouldn?t have to provide a means of disconnection correct? Or do the panels have to be insight of?
 
stuartdmc said:
Ok. I see your point. What year code change was that?

What if I where to hard wire the piece of equipment, would it still need the protection? The panels that are feeding the equipment are within 25ft so I wouldn?t have to provide a means of disconnection correct? Or do the panels have to be insight of?

That has been mentioned but you must be certain that hard wiring a unit that was manufactured with cord and plug may void the UL listing.
 
stuartdmc said:
Ok. I see your point. What year code change was that?

What if I where to hard wire the piece of equipment, would it still need the protection? The panels that are feeding the equipment are within 25ft so I wouldn?t have to provide a means of disconnection correct? Or do the panels have to be insight of?

equipment that is designed to be hardwired doesnt have to be GFCI protected.
 