What did I start oh gosh
Nothing in 210.8 that requires lighting to be GFCI protected other than within crawl space [210.8(E)] but nothing in 210.8 prohibits it either.I will be the devil.
Does this mean that lighting circuits can not be on the feeder? So the feeder has to be specific for a sub panel that only is for receptacle circuits?
Too late, you did it.What did I start oh gosh
All lighting circuits for the house are in the main panel. The only thing I would transfer from the main panel to the sub-panel would be a AC unit & a electric range. [to make room for TVSS and the feeder breaker to supply the sub-panel] Any other circuits in the sub-panel would be the new home theatre room, ie: circuit for the electronic equipment & stereo, circuit for the lighting limited to the room only, and wall outlets required by code for finished off walls.Nothing in 210.8 that requires lighting to be GFCI protected other than within crawl space [210.8(E)] but nothing in 210.8 prohibits it either.
But I have a further question, what constitutes a crawl space? Is it if a 4ft tall person cannot stand upright, is it 5ft, or is it less than 3ft?
Too late, you did it.
I agree with you about 210.8, but the 215 allows the "feeder for receptacle circuits" to be GFCI protected but does not mention lighting.Nothing in 210.8 that requires lighting to be GFCI protected other than within crawl space [210.8(E)] but nothing in 210.8 prohibits it either.
But I have a further question, what constitutes a crawl space? Is it if a 4ft tall person cannot stand upright, is it 5ft, or is it less than 3ft?
Too late, you did it.
The rooms that you are wiring "require" GFCI protected circuit" or "GFCI protected receptacles"?I'm going to just put in branch circuit GFCI breakers in the sub box, it was just a question that I posed to see if I could main it with a GFCI. I'm just trying to learn this new code book and wanted direction. Thanks everyone for the comments & advice.
It's one room, a big home theatre in a basement. I just looked thru the dozen emails from the homeowner and couldn't find the one where the permit was pulled to see exact wording on if "circuit" or "receptacles" need to be GFCI. I'll just GFCI anything new leaving the panel. It's actually going to be finished off basement so by the 2014 code they go by doesn't require it, but I was told somewhere in an email to do it. I'll probably AFCI it also.The rooms that you are wiring "require" GFCI protected circuit" or "GFCI protected receptacles"?
No. The requirement for GFCI is for receptacles. Adding GFCI to lighting circuits is a design choice and not disallowed.I will be the devil.
Does this mean that lighting circuits can not be on the feeder? So the feeder has to be specific for a sub panel that only is for receptacle circuits?
What did I start oh gosh
On this job 1 circuit is up by the ceiling, 2 outlets to feed LED rope lights [on a 3 way] that will circle the room . Maybe 40-50 feet of rope LED's in a soffit to give indirect lighting off of the ceiling to the theatre. I'll AFCI/GFCI it with the other circuits I install. The homeowner will be hanging curtains to replicate a real old time movie theatre like I went to as a kid. So a potential fire hazard.No. The requirement for GFCI is for receptacles. Adding GFCI to lighting circuits is a design choice and not disallowed.
I would.thanks,
so I should just toss a few GFCI single pole breakers into the sub-panel and call it a day?
AC and range? Why would you move the two largest loads the house has to a sub panel? Why not pick lighter loads?All lighting circuits for the house are in the main panel. The only thing I would transfer from the main panel to the sub-panel would be a AC unit & a electric range. [to make room for TVSS and the feeder breaker to supply the sub-panel] Any other circuits in the sub-panel would be the new home theatre room, ie: circuit for the electronic equipment & stereo, circuit for the lighting limited to the room only, and wall outlets required by code for finished off walls.
Nothing in that rule restricts the protection to only receptacle circuits. The rule is just giving the installer an additional method of providing the GFCI protection required in 210.8.I will be the devil.
Does this mean that lighting circuits can not be on the feeder? So the feeder has to be specific for a sub panel that only is for receptacle circuits?
You new around here? We love flogging a dead horse into a greasy spot on the ground. ;^)What did I start oh gosh
You new around here? We love flogging a dead horse into a greasy spot on the ground. ;^)
So even though this jurisdiction is going by the 2014 code, and GFCI isn't required in "finished" off parts of a basement, the AHJ is requiring it. I'd do it anyways.