140428-1016 EDT
kwired:
Magnitude of flux change is the same but there is a difference in the current in the hot lead thru the current transformer.
When the test resistor is connected to hot on the output side, then the hot line current thru the current transformer under test conditions is greater than the neutral current. This is the real world case. When the test resistor lead passes thru the current transformer and terminates on the hot wire input side, then both hot and neutral wires have the same current. The flux is changed by the addition of the the third wire and the current thru it.
.
kwired:
Magnitude of flux change is the same but there is a difference in the current in the hot lead thru the current transformer.
When the test resistor is connected to hot on the output side, then the hot line current thru the current transformer under test conditions is greater than the neutral current. This is the real world case. When the test resistor lead passes thru the current transformer and terminates on the hot wire input side, then both hot and neutral wires have the same current. The flux is changed by the addition of the the third wire and the current thru it.
.