GFCI test button

Status
Not open for further replies.

TVH

Senior Member
Electrical and Safety Professionals have told me that the test button on GFCI receptacles is a test of the mechanical mechanism "only" and does not actually cause a ground fault. I'm also told that "portable GFCI /circuit testers" actually cause a ground fault and these devices should be used by inspectors to confirm the proper operation of a GFCI as well as proper wiring. Would appreciate clarification on this important issue by you folks in the field.
 

charlie b

Moderator
Staff member
Location
Lockport, IL
Occupation
Semi-Retired Electrical Engineer
I believe you have been misinformed. The test button on the GFCI receptacle causes current to flow from the ungrounded ("hot") conductor to the grounded ("neutral") conductor. The GFCI device will then recognize the imbalance between the two conductors and this will result in a trip. The portable GFCI tester will cause current to flow between the ungrounded conductor and the equipment grounding conductor (the green wire). This will also result in a trip. But it will not work if there is no green wire in the circuit. The NEC does allow an ungrounded receptacle outlet that has no ground wire available to the outlet box to be replaced with a GFCI receptacle (you must label the outlet "no equipment ground"). So the GFCI receptacle can be functioning correctly, but a portable GFCI tester will not be able to discern that. The test button on the receptacle itself is the most reliable way to verify that the receptacle is operational.
 

roger

Moderator
Staff member
Location
Fl
Occupation
Retired Electrician
Electrical and Safety Professionals have told me that the test button on GFCI receptacles is a test of the mechanical mechanism "only" and does not actually cause a ground fault. I'm also told that "portable GFCI /circuit testers" actually cause a ground fault and these devices should be used by inspectors to confirm the proper operation of a GFCI as well as proper wiring. Would appreciate clarification on this important issue by you folks in the field.
As Charlie explained, what you have been told is basically in reverse as to what's true. As a matter of fact, for a long time and I think it's still true the only UL recognized way of testing a GFCI device was with the on bard test button.

Roger
 

Dennis Alwon

Moderator
Staff member
Location
Chapel Hill, NC
Occupation
Retired Electrical Contractor
I will also add that the gfci tester will not trip a GFCI receptacle or circuit if there is equipment grounding conductor.
 

Coppersmith

Senior Member
Location
Tampa, FL, USA
Occupation
Electrical Contractor
I have an Ideal 61-165 tester I use for testing GFCI's. It seems to catch many bad GFCI's that don't show as bad when the GFCI's test button is actuated. Does my tester work the same as the GFCI testers you are talking about? I'm assuming you are talking about those cheap ones with the three neon lights in them.
 

don_resqcapt19

Moderator
Staff member
Location
Illinois
Occupation
retired electrician
I have an Ideal 61-165 tester I use for testing GFCI's. It seems to catch many bad GFCI's that don't show as bad when the GFCI's test button is actuated.
What makes you think that your tester is correct and the device test circuit is not?
Does my tester work the same as the GFCI testers you are talking about?
All plug in GFCI testers work the same way. They actually create a ground fault and they can only do that if the receptacle being tested has an EGC that provides a path back to the main bonding jumper.
 

GoldDigger

Moderator
Staff member
Location
Placerville, CA, USA
Occupation
Retired PV System Designer
What makes you think that your tester is correct and the device test circuit is not? All plug in GFCI testers work the same way. They actually create a ground fault and they can only do that if the receptacle being tested has an EGC that provides a path back to the main bonding jumper.
Or if you supply a temporary return connection via an external EGC to another point in the wiring system.
I would not recommend trying to use a foreign neutral connection instead.
 

roger

Moderator
Staff member
Location
Fl
Occupation
Retired Electrician
I have an Ideal 61-165 tester I use for testing GFCI's. It seems to catch many bad GFCI's that don't show as bad when the GFCI's test button is actuated. Does my tester work the same as the GFCI testers you are talking about? I'm assuming you are talking about those cheap ones with the three neon lights in them.
I have a GFCI tester that cost over a hundred and twenty five dollars (I have it for testing hospital Isolation systems) and it is no more a true GFCI test than a 5 dollar unit can do. IOW's, use the on board test button if you want a correct test.

Roger
 

kwired

Electron manager
Location
NE Nebraska
Occupation
EC
The test button does make the device see same condition as seen during a ground fault, but without an actual ground fault.

A resistor sized to draw enough current to be in the trip range of the device is connected with one lead through the current sensing CT and the other lead does not pass through, which unbalances the current in the CT and causes the device to trip if the electronics are functioning correctly. This is why the test button will trip the device even if there is no EGC present. A plug in tester must have an EGC or at least have EGC connected to a path that will carry the needed 4-6 mA to cause the device to trip.
 

TVH

Senior Member
Electrical and Safety Professionals have told me that the test button on GFCI receptacles is a test of the mechanical mechanism "only" and does not actually cause a ground fault. I'm also told that "portable GFCI /circuit testers" actually cause a ground fault and these devices should be used by inspectors to confirm the proper operation of a GFCI as well as proper wiring. Would appreciate clarification on this important issue by you folks in the field.

Thank you gentlemen. Very informative.
 