aside from the customary "test" button that is provided on GFCI breakers and GFCI outlets does anybody know of a real world method that won't physically get you into zapped?
Seems to me that the "test" button is merely a switch a like life safety devices the "test" button being pressed only lets you know that the "test" button makes the circuit. Any ideas?
 

iwire

Moderator
Staff member
Location
Massachusetts
The test button does not just trip the GFCI it really does test it and it is the only UL backed way to field test a GFCI.

All the low dollar gizmos that claim to be testers are just 'indicators' and none of them can trip a GFCI that is used as a replacement on an ungrounded circuit as specifically allowed by 406.3(D)(3)
 

iwire

Moderator
Staff member
Location
Massachusetts
Does that mean the little tester your friendly inspector uses to test your wiring at the receptacles is not UL approved?

UL does not approve anything.

Those things, to the best of my recollection are UL listed as indicators.

They can certainly check if a normal looking duplex is in fact connected to an operational GFCI. But once your at the GFCI itself the test button should be used.

The test button but actually creates a calibrated current imbalance to test the electronics and relay of the GFCI.
 

480sparky

Senior Member
Location
Iowegia
Part of UL 1436 reads:

1.1 These requirements apply to outlet circuit testers, including screwdriver and pen-style voltage presence indicators, for use on 15-, 20-, and 30-A, 3-wire, 125-, 250-, 277-, 480-, or 600-V receptacles, ground-fault circuit-interrupter testers and arc-fault circuit-interrupter indicators for use on 15- and 20-A, 3-wire, 125-V receptacles, and similar indicating devices that are:
a) Intended to be connected to the receptacle for a period of time only as long as is necessary to note the indicated pattern of lights or other similar indicating means, and
b) Not intended to be a comprehensive instrument or to determine the quality of the grounding circuit.
 

gar

Senior Member
Location
Ann Arbor, Michigan
Occupation
EE
090712-1329 EST

The Leviton 7899 has a very interesting test function.

Pressing the TEST button mechanically unlatches the mechanical latch. This is all that is tested at this point.

When the RESET button is pressed the electronics and functionality of the trip coil are tested. If this fails the unit will not latch.

To me this seems better than doing the test of the electronics when the TEST button is pressed. In the Leviton design you are testing the electronics any time the device is RESET at the time of RESET and not just when the TEST button is pressed.

Internally some, if not all, GFCIs use a 15,000 ohm resistor from hot on the output side of the current transformer to neutral on the input side of the current transformer to create an unbalanced test current of 8 MA at 120 V.

You could do your own external test with a 15000 ohm resistor connected from a neutral or EGC that precedes the device under test to a hot slot in the device under test.

.
 

LarryFine

Master Electrician Electric Contractor Richmond VA
Location
Henrico County, VA
Occupation
Electrical Contractor
You could do your own external test with a 15000 ohm resistor connected from a neutral or EGC that precedes the device under test to a hot slot in the device under test.
I just use my wiggy (K-60) as an external tester.
 

iwire

Moderator
Staff member
Location
Massachusetts
I just use my wiggy (K-60) as an external tester.

I have done that many times myself but I would call that an indication not a test.:smile:

I think it is safe to assume the running load of wiggy at 120 volt is far above 8 ma and the inrush well above that. :smile:
 

don_resqcapt19

Moderator
Staff member
Location
Illinois
Occupation
retired electrician
Gar,
Is that the newer design GFCI with the "lockout function"? It sounds like it is, and the description would prevent the GFCI from providing power to the outlet if the electronics have failed, providing a safer installation. In the older design GFCIs, you could reset them even when the electronics could no longer provide the required protection.
As a side question, did your testing indicate that the device would kill the output power if the electronics have failed. My understanding is that they do not and the only provide the "lockout protection" when you try to reset them after a test or trip.
 

gar

Senior Member
Location
Ann Arbor, Michigan
Occupation
EE
090712-1718 EST

don:

This is clearly a newer design and does have the lockout function.

Certain types of electronic failure in this device will cause a trip.

I will suggest that there is no way to design any product such that every possible failure mode will cause a failure to a safe condition.

In fact you may not be able to define a safe condition. Suppose you have a machine in which a person is caught. Should an emergency stop button cut all power, or is it better to leave the machine power on and automatically shift to manual mode. My suggestion --- do not get caught in the machine. That is the safest approach.

On some machines with light curtains, where I had some input on the control design, and where the machine cycle was such that manual entry during the cycle was part of the cycle it was possible to check the light curtain at least once per machine cycle. This was done by knowing that at certain points in the cycle that manual entry was required and thus a change of state should occur. If this change did not occur the cycle was inhibited. Normally light curtains only do a self test at power on. This was some years ago. It may be that some new designs have created ways to do self tests at times other than power up.

.
 

cpal

Senior Member
Location
MA
Back in the 70's we had a meter that dialed in the mA to Gd. to prove the GFCI breakers (prior to rec) good. Are they still around???
 

LarryFine

Master Electrician Electric Contractor Richmond VA
Location
Henrico County, VA
Occupation
Electrical Contractor
I think it is safe to assume the running load of wiggy at 120 volt is far above 8 ma and the inrush well above that. :smile:
I believe the K-60 has a 4K impedance, which would have about 4x the current of the resistor.

What about the typical 3-prong plug-in receptacle indicator/GFCI tester?
 

hurk27

Senior Member
I have done that many times myself but I would call that an indication not a test.:smile:

I think it is safe to assume the running load of wiggy at 120 volt is far above 8 ma and the inrush well above that. :smile:

I thought we have already determined that any external tester only served this very function? if so why by a GFCI tester when a wiggy will serve the same purpose, I mean its not really testing the function of the GFCI but just indicating that a said receptacle is in fact protected by a GFCI device:grin:
 

hurk27

Senior Member
i have the slater gfci tester. is that the one your talking about? it dials in the trip current

It was a greenlee, yellow, and black case with a short pigtail to plug into an outlet.
It would send a pulse every 5 sec. at the rated set setting so you could reset the breaker and make sure it trips twice, why? I have no idea they design it that way.
 
Last edited:

ELA

Senior Member
Occupation
Electrical Test Engineer
090712-1718 EST

On some machines with light curtains, where I had some input on the control design, and where the machine cycle was such that manual entry during the cycle was part of the cycle it was possible to check the light curtain at least once per machine cycle. This was done by knowing that at certain points in the cycle that manual entry was required and thus a change of state should occur. If this change did not occur the cycle was inhibited. Normally light curtains only do a self test at power on. This was some years ago. It may be that some new designs have created ways to do self tests at times other than power up.

.

Light curtains have progressed Gar,
http://www.triadcontrols.com/superlight_vi_description.html
 

hornetd

Senior Member
Location
Maryland
Occupation
Journeyman Electrician, Retired
I tested my Wiggy.

I tested my Wiggy.

I have done that many times myself but I would call that an indication not a test.:smile:

I think it is safe to assume the running load of wiggy at 120 volt is far above 8 ma and the inrush well above that. :smile:

Well, just for drill I ran my Wiggy through a current multiplier loop and threw a peak holding Fluke meter on it. Mine actually drew nine milliamps and the meter did not detect any inrush.
 