There is a technological incompatibility between common loads in the home and GFCIs. The incompatibility is often realized in the form of “nuisance tripping”, where a GFCI trips and no electrical hazard is present. This incompatibility is especially pertinent in the context of home appliances, which are subject to continuously updated, mandator
 

Attachments

  • Proposed_TIA_1748_NFPA_70.pdf
    1.4 MB · Views: 28

brycenesbitt

Senior Member
Location
United States
Yeah, discussed elsewhere also. See this PI 1802-NFPA 70-2023, which references this TIA.
I'd like to see either side show real cost/benefit numbers rather than just positional arguments.
And look at alternative ways to achieve the same safety goals, where a safety issue can be demonstrated.
 

Attachments

  • NEC Section 625.54 GFCI and EVSE Exception Proposal.pdf
    204.6 KB · Views: 2

mtnelect

HVAC & Electrical Contractor
Location
Southern California
Occupation
Contractor, C10 & C20 - Semi Retired
There is a technological incompatibility between common loads in the home and GFCIs. The incompatibility is often realized in the form of “nuisance tripping”, where a GFCI trips and no electrical hazard is present. This incompatibility is especially pertinent in the context of home appliances, which are subject to continuously updated, mandator

I am in the process of transitioning to "Insulting Work" ... If I was still doing contracting, I would think about putting a disclaimer on the invoices "After Gound Fault Circuit Interrupters or Arc Fault Circuit Interrupters are installed per code, we will only under our warranty respond once without charge".