This is more of a safety question, rather than a code question. In fact, I doubt the CEC (I'm currently in Canada), or NEC would apply because of the manner in which I solved my problem. Still, I'd appreciate comments regarding the safety of my solution.
I had a nasty ground loop between satellite dish ground and AC safety ground third pin grounding of a subwoofer with a plate amp. Unlike all other home entertainment devices, which are double insulated and thus do not require (nor have) a three pronged AC power cord, the subwoofer uses an "plate amp" with exposed metallic chassis back and a three-pronged AC plug.
In Ontario, unlike the rest of Canada and the U.S. there is no requirement to ground an antenna to a ground electrode, bonded to the rest of the building's grounding electrode system: Bonding to a cold-water entry pipe within the building within a certain distance of entry is sufficient. I think the reasoning is that the purpose of the ground is to discharge static rather than offer lightening safety, since even with a ground rod, a direct strike would still be devastating. I bonded mine to a point on such a pipe within two inches of where the house AC entry is also grounded (yes, code permits this as well here).
Alas, I still had a ground loop via the subwoofer AC ground. I considered breaking the loop by replacing the permanent AC outlet supplying power with a GFCI, and not grounding the GFCI, but this is only acceptable if there is no ground wire to begin with. Instead, I fashioned an adapter, with a 6 foot cord terminated in a two pronged AC plug, to a non-metalic single-gang box, where I installed a GFCI, ungrounded (obviously). I also applied one of the "not grounded" stickers supplied with the GFCI to this box. Using this "extention cord", I can break the ground loop to the subwoofer with no permanent wiring change. I figure that if a short to the plate amp chassis were to occur, the GFCI would trip.
Naturally, the AC cord for this extention is rated to the current capacity of any outlet in which it can be plugged (as is the GFCI, by design). The trip limit on the GFCI is 4-6 mA. With the two pronged plug and clear labelling of the GFCI as ungrounded, I can't envision ever confusing this as an extention that preserves a safety ground.
So, just how bad a boy have I been?
I had a nasty ground loop between satellite dish ground and AC safety ground third pin grounding of a subwoofer with a plate amp. Unlike all other home entertainment devices, which are double insulated and thus do not require (nor have) a three pronged AC power cord, the subwoofer uses an "plate amp" with exposed metallic chassis back and a three-pronged AC plug.
In Ontario, unlike the rest of Canada and the U.S. there is no requirement to ground an antenna to a ground electrode, bonded to the rest of the building's grounding electrode system: Bonding to a cold-water entry pipe within the building within a certain distance of entry is sufficient. I think the reasoning is that the purpose of the ground is to discharge static rather than offer lightening safety, since even with a ground rod, a direct strike would still be devastating. I bonded mine to a point on such a pipe within two inches of where the house AC entry is also grounded (yes, code permits this as well here).
Alas, I still had a ground loop via the subwoofer AC ground. I considered breaking the loop by replacing the permanent AC outlet supplying power with a GFCI, and not grounding the GFCI, but this is only acceptable if there is no ground wire to begin with. Instead, I fashioned an adapter, with a 6 foot cord terminated in a two pronged AC plug, to a non-metalic single-gang box, where I installed a GFCI, ungrounded (obviously). I also applied one of the "not grounded" stickers supplied with the GFCI to this box. Using this "extention cord", I can break the ground loop to the subwoofer with no permanent wiring change. I figure that if a short to the plate amp chassis were to occur, the GFCI would trip.
Naturally, the AC cord for this extention is rated to the current capacity of any outlet in which it can be plugged (as is the GFCI, by design). The trip limit on the GFCI is 4-6 mA. With the two pronged plug and clear labelling of the GFCI as ungrounded, I can't envision ever confusing this as an extention that preserves a safety ground.
So, just how bad a boy have I been?