ptonsparky
Tom
- EC - retired
Related to 'VFD & GFCI'
I decided to test the trip levels of my small GFCI protected splitter. I've had it for years,+ a couple more, and typically use it with a small genset or locations that have no GFCI readily available.
My poor mans method is to use my Fluke 87 on the ma range and catch the MAX values of a Neutral to EG fault via the meter. I then compared it to a newer GFCI receptacle on my work bench.
100 msec. Yes, I know pressing the Test Button occasionally is all that I am required to do.
Splitter: 9.6, 7.2, 4.8, 3.2, 7.2
GFCI: 4.8, 4.8, 5.6, 4.8, 4.8
The old splitter is headed to the scrap barrel but I am wondering if the new self testing GFCIs actually check the levels at which it trips?