180324-1144 EDT
An experiment:
Leviton GFCI receptacle. AC power, nominal 120 V, continuously applied to Line terminals. No load on load terminals, or recreptacle sockets.
A series circuit of a 6 V transformer secondary (transformer provides isolation), a 5 k pot in series with a 220 ohms 1/2 W resistor, and a Fluke 27 in AC mA mode. This series circuit is connected between "line neutral" and "load neutral" of the GFCI.
Power to the 6 V transformer is applied and removed to perform each test. This is not a requirement. My procedure had the transformer power off when the GFCI was reset.
I started each test at abourt 3 mA, not precise, not important, just needs to be somewhere below the trigger point. Note: I had no current at time of reset, but the series circuit is connected to the two neutral terminals.
Test:
Test current zero, but the test current circuit was connected.
GFCI RESET.
Applied test current starting at about 3 mA.
Gradually increased test current to around 4.8 mA where GFCI starts to try to trip, but does not.
At about 4.9 mA the GFCI trips. There seems to be less than about 0.1 mA variation in the trip point on multiple trials.
Remove test current.
RESET GFCI.
Repeat.
.