Hi, not sure if I worded that right but I was at a house doing a service call and was ask to install an outside outlet...I tapped off an existing recepticale on the oppisete side of the wall and installed a weatherproof j-box and a GFCI then a bubble cover. I put in a gfci receptacle tester and pressed the test button on the tester and it shut off the power to a gfci upstream in the upstairs bathroom I did'nt realize was even there. I was surprised it didn't shut off the gfci I was testing instead of the one upstream of the one I just installed. Is this how it works? I thought it should shut off at the one I was testing with the plug-in tester??? The gfci in the bathroom is controling outlets all over the house, upstairs bed/bathroom and outlets in downstairs bathroom and living room and I think I should disconnect what's coming off the load side of it and install any other needed gfci's independantly. Thanks, JB