z = 240v/4mA = 60k; 4 mA low limit of GFI
= 1/(377*C)
C= 44,000 pF ; (0.044uF)
44k/250 ft = 176 PF per foot for UF 10/3 ???? (to lazy to go to the shop with capacitance meter this late/early and measure a roll<G>)
Unless I dropped a zero, methink the tripping NOT due to capacitive current - Unless there are a LOT of higher frequency harmonics.
A GFCI will trip on the difference of the L-G leakage currents on the two conductors, and this would be the current through the excess amount of L-G capacitance on one side when 120V is applied across it. And so to produce the 4 mA low limit trip current, 0.089uF more L-G capacitance on one side than the other would be required. In other words this would be the minimum amount of unbalanced L-G capacitance on the two conductors before a trip could possibly occur. I agree that the capacitance per foot required for this seems too high, especially since we are talking about the amount of unbalanced capacitance and not the L-G capacitance itself.
To make sure there are no other factors involved I did some testing. I applied a fault current from line to ground on the output of a 120V GFCI receptacle using various capacitors.
As I increased the capacitance it started buzzing, but it still did not trip with 0.185uF which would draw 8.4 mA at 120V 60 Hz. It tripped when I reached 0.205uF which would be 9.3 mA of leakage at 120V 60 Hz.