Dear All,
I have two separate GFCI Outlets (Two Phoenix contact Part#5602519) in my Network cabinet. Both of them feeds Eaton UPS Downstream (One outlet feeds one UPS) . And the UPS Feeds Network switches and the Network PC.
During power outage the batteries will die and cabinet powers off. During this event one of the GFCI trips. Each time the power is back, the network cabinet is Off and we need to reset one of the GFCI Outlets . Same outlet trips all the time . Not sure the GFCI trips when the battery dies or when the power is back.
Does inrush current of UPS (overload ) trips GFCI outlet? or is there a chance of variation if current flowing through Hot and neural conductors going to the UPS or downstream that causes the GFCI trips. The second GFCI is just a redundant circuit with less load. That GFCI doesn't trip.
My Circuit is 115VAC. 3 Conductors - hot, neutral and ground
Why is one GFCI Tripping? If any info please help
I have two separate GFCI Outlets (Two Phoenix contact Part#5602519) in my Network cabinet. Both of them feeds Eaton UPS Downstream (One outlet feeds one UPS) . And the UPS Feeds Network switches and the Network PC.
During power outage the batteries will die and cabinet powers off. During this event one of the GFCI trips. Each time the power is back, the network cabinet is Off and we need to reset one of the GFCI Outlets . Same outlet trips all the time . Not sure the GFCI trips when the battery dies or when the power is back.
Does inrush current of UPS (overload ) trips GFCI outlet? or is there a chance of variation if current flowing through Hot and neural conductors going to the UPS or downstream that causes the GFCI trips. The second GFCI is just a redundant circuit with less load. That GFCI doesn't trip.
My Circuit is 115VAC. 3 Conductors - hot, neutral and ground
Why is one GFCI Tripping? If any info please help