ELA
Senior Member
- Occupation
- Electrical Test Engineer
RusticKris,
A couple of people have questioned if you really have 120VAc to the receptacle in question. I missed where you stated the measured voltage? ( preferably under some load)
The GFCI does a test, to see if it can trip, when you push reset. The success of this test is dependent upon the line voltage level at the time.
( test is also depended on whether there is leakage on the load but you seem to have eliminated this since there is no downstream load)
I tested this function on a Leviton GFCI a while back. Results will vary some from device to device but in the one I tested anything below 108V started to get erratic.
At a 100-108V the reset button chattered a bit as it was reset , but did reset. At 95V it struggled to reset. Anything below 90V and it would fail completely.
Assuming you do measure a supply above 108V ( under load) does the unit chatter excessively as you attempt to reset it?
Your test results, on a separate line cord, will be helpful.
A couple of people have questioned if you really have 120VAc to the receptacle in question. I missed where you stated the measured voltage? ( preferably under some load)
The GFCI does a test, to see if it can trip, when you push reset. The success of this test is dependent upon the line voltage level at the time.
( test is also depended on whether there is leakage on the load but you seem to have eliminated this since there is no downstream load)
I tested this function on a Leviton GFCI a while back. Results will vary some from device to device but in the one I tested anything below 108V started to get erratic.
At a 100-108V the reset button chattered a bit as it was reset , but did reset. At 95V it struggled to reset. Anything below 90V and it would fail completely.
Assuming you do measure a supply above 108V ( under load) does the unit chatter excessively as you attempt to reset it?
Your test results, on a separate line cord, will be helpful.
Last edited: