Several years ago, I came across a situation at a big-box retailer where turning on an Advance T8 florescent ballast caused the near simultaneous GF trip of its circuit breaker and seven other SquareD GFCI breakers in a 42 ckt QOB panel.
I one-lined the circuit and it was dedicated to the ballast in a new display case. Somehow the ballast was tripping the other GFCI's from the line-side. I changed the ballast to a Triad or such and the tripping stopped.
In the OP's situation, there doesn't appear to be a switched load on a different circuit that is causing the trip. But I've never seen this occur at a GFCI receptacle.
I one-lined the circuit and it was dedicated to the ballast in a new display case. Somehow the ballast was tripping the other GFCI's from the line-side. I changed the ballast to a Triad or such and the tripping stopped.
In the OP's situation, there doesn't appear to be a switched load on a different circuit that is causing the trip. But I've never seen this occur at a GFCI receptacle.