J jbarr New member Jan 9, 2004 #1 Is GFCI protection required on all radiant cable heat? I am installing radiant cable heat on dura-rock to be covered with ceramic floor tile, but I can't find an article that covers over current protection.
Is GFCI protection required on all radiant cable heat? I am installing radiant cable heat on dura-rock to be covered with ceramic floor tile, but I can't find an article that covers over current protection.
don_resqcapt19 Moderator Staff member Location Illinois Occupation retired electrician Jan 9, 2004 #2 Re: GFCI GFCI protection for the heating cables is required in bathrooms, and in hydromassage bathtub, spa, and hot tub locations. See 424.44(G). Don [ January 09, 2004, 02:55 PM: Message edited by: don_resqcapt19 ]